Maintenance Structure - Backup with error FFLibraries
When the full backup finish, it show an error from FFUpload. "H1_LCP_1100: An error occured. Return value hr=0x8000401a". When I open FFBuilder, all network is fine. How I can fix the error?
Voted best answer
I'm come across this error also.You need to install the device management foundation fieldbus to this node. Previous node have this extension
Answers
Hello,
If interactive user is not logged in the system(Primary aspect server) where backup is running then there are chances of failing of backup execution when you try to take the backup from other than primary aspect server.
This problem gets corrected in 5.1Fp4 rev E.
try taking backup from Primary aspect server.