License signals calculation with compact HMI
Hello,
I have a question about the license calculation for compact HMI. In this topic (http://www402.abbext.com/Licence-Tag-...) they say that the license calculation for Compact HMI is based on Tags instead of Signals. But is this also when you use PLC Connect or only when you use OPC? It is hard to find a good answer in the manuals.
I want to make a connection with an AC500 PLC.
Answers
AFAIK, count faceplate aspects outside Object Type Structure.
Use afwsysinfo.exe, Find Tool or Bulk Data Manager to count.
PG2 or VB6 faceplate does not matter - an object outside OTS having one or more faceplate aspects will require one (1) TAGS count.
No faceplates = no requirement for TAGS.
Ensure .SLA file has TAGS or RED_TAGS with same or higher number than what you found when searching.