OPC Time Stamp AC800m
Hi,
It is possible to configure the OPC Server from ac800m (compact) to send to clients the time stamp from the plc and not the machine?
In case of yes, I've never configured time for this plc, wich manual I have to read for both items?
Thank you.
Voted best answer
The AC800 OPC server uses the local computer's clock when timestamping OPC DA data(OPC AE alarm&events are sent with time stamps from the controller).
Please read the System 800xA Network Configuration user's guide (3BSE034463-510) - it explains how time can be brought from the controller to the computer or vice versa using NTP, CNCP and MMS (the time protocols available in AC800M).
/Stefan
Answers
Hello
For controller time configuration ( Synchronisation ) please refer to 3BSE041584-510 Compact 800 Engineering
Compact Control Builder AC 800M 5.1 , page 129
https://www.google.co.in/?gws_rd=cr&ei=MtJCUtyyM4XC4AOwsIHYCg#psj=1&q=+
abb+3BSE041584-510
and for OPC DA+AE configuration
refer 3BSE035983-510 AC 800M
OPC Server
Add new comment