Parameter error CI801
I am trying to set up IO-node from Freelance AC900F, to an profibusslave with CI801. But HW-config says "Parameter error on slave". I have tried with three different versions of GSD-file. Anyone has any input in this question would be helpful?
Best regards Magnus Bergsten
Voted best answer
Hello,
more information requested via comment will help in getting you correct answer,
however try associated app here, there are templates available for CI801 and i/o modules so instantiate preconfigured hardware...and let see if that works...
Note you need at least one I/O module along with any PB slave, also incase you are using morethen one I/O modules module position needs to be set manually under user parameter tab, bydefault all module takes position 1.
Also lastly check the configured and physical address is matching....for CI801 node you are setting up...
by Dieter Henkel
Please provide some more information. Which Freelance Version are you using? Can you provide a screenshot from the Hardware manger of your Profibus and Slave configuration?
by MagnusB Rank: 802 on 7/19/2016 5:56:08 AM | Like (0) | Report
I am using ABB Freelance 2016 with AC900F, CI773F profibusmaster.