Error indication on IO modules of RTU560
Hi I am using 560MPR01 with 560CMR01 communication card along with 23AE23 (Analog Input card) and 23BE23 (Binary Input card). All the IO cards are showing RED indication on LED. Also in in Communication card ERR status is with RED blink. May I know how to clear the errors on IO card.
I am getting the warning message during consistency check as "No reference to IO bus configured for rack 560MPR01"
Voted best answer
Hi.
2 reasons are possible for this error. 1st you didnot configured the IO cards & still uploading the rcd file in rtu(which is less likely to happen). 2nd n most likely reason could be that you had exceeded the allowed number of data data points as per your licence. for exampleif you have licence for 250 data points n in your rtu software you had configured lets say 270 data points then when you upload the rcd filein rtu, it will go in error mode. all cards red LED will glow.
Allowed number of data points are mentioned on the memory card.
Hope this will help
by admin Rank: 37 on 7/12/2016 6:35:28 PM | Like (0) | Report
Post microscada and IED related questions at following portal @ https://abb.custhelp.com