Good Evening to All,
I am new to this process "Generating Reports". I have to create a daily report format for few parameters like V,I,Kw,KVA,KVAr. I need 1 reading per hour thus creating 24 reading for a day for which I created an excel template with settings as shown in Pic 1 with No. of values=24 & start time as Dynamic Now-24 hours.(Please correct me if I had done it wrong) & in job description it is planned to run every 60 mins.
Report generation should start at 22.00
what I thought an excel file will be generated after 24 hours with 1 set of readings per hour but a number of excels are being generated with interval of 1 or 2 hours.
Can someone please correct what wrong I had done in my process or what changes in settings are required to generate a daily report
Thanks & warm regards
Answers
>"job description it is planned to run every 60 mins."
So if you run a job every 60 minutes you get 24 reports per day. Thats exactly what you programmed it to do.
Run one report every 24 hours at 22:00 using SAMPLED data from the logs. Make sure the logs sample every few minutes - You want the actual sampled value closest to each hour, not an interpolated value between two samples.
The 800xA system provides a number of templates for reports contained in the Scheduling Structure. I have included a document that details how to configure and generate one of these reports that provides one hour averages of up to 20 data points per report, (you don't need to configure all 20 if they are not needed). Additionally, I have included a slightly modified version of this report and a sample of the output with only two variables configured.
Regards,
Geof