How to communicate with siemens relay with abb 800xa on IEC61850 protocol
Hello,
One of our client has the requirement for only to monitor the status of siemens relay located at their 1 substation and communicating with siemens scada. They want the status of those relays to be seen in IEC61850 based 800xA system Without effecting their existing communication system.
Can someone provide me with some document how we can achieve that.
Thanks
Answers
Greetings,
You can use Kepware (supports IEC protocol) and PLC Connect. We did this at the past with this way.
You obtain SCD file from web interface of the relay or DIGSI from at the same time you notice that firmware version of the SCD file of the relay. I recommend customer connet ot the relay and they give to you this file if you do not set up relay program. After that u import this files inside kepware and then you must watch this values with kepware quick client. If you do not watch these values you want to siemens a program to watch this. Siemens will give this program to check these values. After that you connect from 800xa to kepware with PLC Connect. You can use PLC Connect Aks or manuel easily from google. Good luck
Use IEC61850 Connect of 800XA.
But the relay need to support multiple clients. Take the SCD file from the customer , look the number of client available, if you have spare client then use that one to communicate ABB IEC61850 connect.