Is it possible to integrate System 800xA with Matricon IEC61850 OPC Server?
Hi,
I am trying to communicate a REF615 IED to 800xA using Matricon IEC61850 OPC Server.
While from the OPC Server directly i am able to monitor the IED, not able to integrate the same to 800xA. After uploading the scd file in 800xA, the conducting equipment under the subnetwork is not reflecting.
Thanks in advance
Answers
This is not the same as the 800xA IEC61850 connect, where you can import the SCD file directly into 800xA AND you get both horizontal and vertical commuincations with Goose. Using the Matrikon product give you OPC access to the data, same as any PLC. Therefore this consideration must be taken into account. If this is what you want then, yes you could use the Matrikon product. But I would ask why?