Download Logic from AC800M Controller
Hi ,
Is there any way to download logic from AC800M Controller ?
Engineering project PC is crashed and AC800M Controller is running, any way we can downlaod the logic.
This is compact product no HMI not 800xa
Regards
Voted best answer
Nope.
Where's your backup ?
Otherwise you're looking at specialist recovery services to get the data back from the disk ( if its recoverable ) Typically $1K to 2K even if no data is recovered. If the disk is fire or water damaged or the heads crashed onto the surface then theres literally zero chance of ever getting your data back.
Where's your backup ?
Answers
PLC to PC is named upload and it is not possible for ABB controllers (and probably it will not be).
In case if you have a valid CF in the controller, you can copy it to have a backup of the now running application. But is is not possible to upload, modify or other action on it. It is intended only to load the application and run the controller.
Normally, I save by using of Explorer the backup of application (CBM files,SCADA backup, panel project) on this CF too - just in case.