HART DTM for Multivariable Trasnsmitter ABB 2010TC
I need a HART DTM file for ABB multivariable Transmitter 2010TC series, to work with system 800xA version 5.1.
I tryed with the DTM file: 2PAA100918S05_A_en_System_800xA_ABB_267_269_V1.2_DeviceObjectType-HART.exe but don't have results.
the DTM file don't support the data of the multivariable transmitter.
I tryed with the DTM file: 2PAA100918S05_A_en_System_800xA_ABB_267_269_V1.2_DeviceObjectType-HART.exe but don't have results.
the DTM file don't support the data of the multivariable transmitter.
Answers
Hello,
The object type that you have used (2PAA100918S05) is the latest & correct one.
It corresponds to the Device Revision 2 of 2010TC (also known as Device Types 267_269).
Are you using device revision 2 ?
In case you are using any other device revision, pls send a request to DIC@in.abb.com with the following data:
Device Manufacturer
Device model / Device name (Preferably Device ID, in this case it should be 0x8A)
Device Revision
Project Name , Sentinel ID
800xA System revision
thanks,
neil shah