SmartClient scale for trends
Dear all,
we would like to force "floating" type for all trends for our smart client clients.
So we modified toolbal panels.sxl (in SC\Files\System\Toolbar Panels\), and tried other files...
However, the type is still "Fixed" and users have to changed each time by opening the configuration mode (time consuming).
Could you help us on this point?
Thanks in advance
Regards
Answers
Could you clarify the question you are asking.
1) Are you asking if the Trend Scales can be made to Auto-Scale relative to the Trace High & Low values in the Scale Factors?
2) Is this for Native Trends created in the Smart Client user interface or is it for Trend Displays imported from an 800xA system, or both ?
3) Have you utilized the Trend Zoom feature as an alternative to changing the Scale Factors? (See Attachment)
Regards,
Geof
Dear Geof,
here are our answers:
1) Yes we would like to have the same scales as our 800xA trends
2) It is for trend imported from an 800xA system
3) Yes, we used this tool but is it possible to have the high/low value of datas without making zoom?
Hope it is clearer.
Regards