OPC server
Hello !
I want to connect my AC700F with a Shneider Electric controller. To do this, I suppose I have to use an OPC server.
Is there any tutorial or explaination for using an OPC server with Control Builder 2013 ? I don't know how to use it.
Thanks !
Eric
Answers
Best way for a controller-2-controller connection would be a serial modbus (ASCI or RTU)or modbus TCP (Ethernet) connection. AC 700 can be both, Modbus master as well as slave.
If you want to use an OPC server, you would need one in the Freelance system and one in the Schneider System and one data pump sitting over both OPC servers to read data from one OPC server and write it to the other systems OPC server.
Dear Eric:
Please find attached file named "3BDD012511 Engineering - OPC Server F" for your reference. As I know, this is a standard manual which delivered with the CBF2013 installation software.
BR/Baogen
Thank you for your answers !
I didn't find the manual, but I will continue to look for it.