Hi, I'm having trouble with Panel PP877. After downloading application from Panel Builder to Panel PP877, I get message: "Failed to create OPC Server: ABB.AC800MC_OpcDaServer", which was chosen during Panel Builder's project creation wizard. Is it possible to simulate PLC with SoftController in this configuration, so that OPC is running on PC, and that panel application can be tested on real Panel using values from OPC?
/ih
Answers
The solution was not found, moreover, communication on real hw didn't seem to work through OPC. We are able to comunicate with our PP877 only via COMLI protocol, if anyone is interested in detailed configuration for this type of communication, let me know.
Greetings,
OPC server is available only when you are using PC Based clients.

For more detail please refer to:
https://library.e.abb.com/public/4e3c...
Hope it helps you.
OPC server is available only when you are using PC Based clients.

For more detail please refer to:
https://library.e.abb.com/public/4e3c...
Hope it helps you.