Fail to "Test" new config. when making an "Online configuration"
I have made small changes to a CLD in Composer 6.1, and compile returns without warnings or errors. When I make an "Online configuration" everything works fine until its time to "Test" the new configuration, the test starts fine but after a short while I receive an error saying "Fail testing new configuration - (GoBack to get out off error mode)", and when I click GoBack I get a "Online Configuration Fatal Error" saying to check the status of the controller e.t.c. before atempting to do a Online config again. I have checked the controller and it seems to be working fine. Our network is a Bailey Infi 90 and the controllers are IMMFP03
Answers
Look at the problem and status reports of the controller when the back up MFP goes to error mode. It most likely has the cause. You can get to them from three Inspect window or under Runtime of the controller.