Acquisition HART data direct to AC800M
Hello,
Please help me in this case:
I need acquisition HART data (HART variable 1 and HART variable 2) to AC 800M from AI815 connected by Profibus.
I know that I can acquisition HART data to 800xA operator workplace and engineering station.
But In this case I need acquisition HART data directly to controller AC800M for use in functional blocks for some calculations and after send to control function block.
I know this option have in Siemens PLC.
May be anybody meet with task like it?
Thank you in advance.
Best regards,
Voted best answer
you can not use the HART data from devices in the controller directly because the HART data is not interpreted by the S800 IO. Instead, you should use S900 IO.
regards,
neil