Is there any 800xA OPC AE Server which can be give to thirparty system.
Answers
Hello,
Maybe I misunderstand your question, but in 800xA Configuration manual:
OPC DA Program Identities
The Program Identity for the System 800xA OPC DA Server to be used by third
party OPC DA clients is ABB.AfwOpcDaSurrogate (local server).
When a new client connection is established the new client will share a running
ABB.AfwOpcDaSurrogate process if possible. If not, a new process will be started
for the new client connection. Use the DCOMCNFG tool to set the DCOM security
setting, see DCOM Security Settings for OPC on page 447.
/Ronny
Please refer to 800xa_5.1 configuration document page 474.
Yes there is an OPC AE server, it is "ABB.OPCEventServer" If you were to browse for it using a OPC AE client, but it should be noted you need a license for a 3rd party application to access it.
Source: 3BDS011222-600 Pg 478
by Stefan Stromqvist
Sad that you did not try looking in the users guides before asking.
Your question is easily answered by reading up a bit.