HART DTM File.
I got a DTM file from the Foxboro website which is not recognised by 800xA device library wizard.
Is there any alternate way to install the DTM file.
Thank you.
Voted best answer
Both previous answers are correct. Let me give a bit more detail. On the DVD which came with the System Software there is one specific for Hart Devices (also if you dont have the DVD you can browse solution bank for your device). If the device of foxboro is available you can copy the zip file to yopur PC and install through the library wizard on every node which uses the DTM. Remember this zip file is delivered from ABB (DIC). If the file is not available then as suggested you can only use the Hart Generic transmitter and so get the standard information from the HART Device. You may also contact your ABB sales representative requesting him to add the device in the list of DIC (Device Integration Center) to get the zip file from ABB in the near future.
Answers
Hi,
Use generic hart dtm from solution bank.
It would help.
DTM files from vendore cannot be used in 800xA system, You need to build device type for 800xA. Either you can use Generic HART DTM or you can contact support line and request to build Device Type for the specfied device..