Download Program for PLC PM554-T
Hi Mr.Gargav,
I have PLC AC500 PM554-T (code: 1TNE968900R0100), but i don't know version (V1.3 or V2.x) so that I don't know use software to program for it (Control Builder plus V1.3 or V2.x ?). What' cable be used to connect between PC and Controller when download program. How to download program? Please support for me! Thank so much!
Voted best answer
Hi!
You use a TK503. USB to seriel.
The driver to the cable TK503 is included on the dvd/usb with Control builder plus v 2.xx. Read the readme before installing the cable!!!
For firmware 2.xx
I've attached a first project pdf that explain how to make the connection(page 18).
For 1.xx
If it is a firmware version 1.3x then you need to only start Codesys.
Use your windows start-->programs-->3S software-->Codesys verison 2.3
The setup of the communication port is like in the PDF.
br
Gustav
Answers
Hi you can use both cable along with USB to Serial Cable,
TK503 cable for COM1 and TK504 for COM2 Port. Driver software for this cable is included in the Software CD.
To find out the PLC Version, read the Code No like "1TNE968900R0100" which printed on PLC , If the code no. ended with 100 series then it will be version 1.3 and you can use Codesys 2.3 software. or code no. ended with 200 series then it will be version 2.x and you can use Control builder Plus.
In your case, the version of PLC is 1.3 and software for the same is Codesys 2.3.
Use your windows start-->programs-->3S software-->Codesys verison 2.3.
To make the communication setup, refer the attached PDF file.
Add new comment