Regarding Property Transfer From 800xa system to freelance system.
I am having 7nos. of AC900f controller which are define in a single logic tree as shown in attached pic ( ie. C1 is 1st controller, C2 is 2nd....C7 is 7th controller) and 800xa for scada, Data transfer from freelance to 800xa system are done through GATEWAY, Now i want to do property transfer from 800xa system to freelance 2013 system,
Following points for detailed information,
1) I am having 3 systems, 1st system consist of Freelance 2013 software, 2nd consists of 800xa software, 3rd system is client system where i have to fetch data through opc.
2) Freelance system and 800xa system are connected through L2 Switch, 800xa system and client system are connected through FIREWALL.
3) I have Done Data transfer from Client system to 800xa system through DCOM setting.
4) Now i have to Transfer the same data from 800xa system to Freelance System, How to do it?
suppose if i need to use OPC tunneler for this, in which two system i have to install tunneler software?
and if there is any other way to tranfer data, kindly guide with notes.
and also if i have to install tunneler in 800xa system wheather it will affect the existing DCOM setting which are done for DATA transfer from client system to 800xa system?
Answers
Hello,
Sorry for late answer, but come across this question now...
Ans 4) in Freelance system Just reference to AC 800M OPC i.e in OPCS give system 800xA (AC 800M OPC IP address) and configure the OPC tunnel in Freelance system. make sure all both IP's are in same subnet...
otherway round if you want Freelance data into System 800xA then use 'Freelance Connect' . Hope that helps...
Find some text from one of the conversation may help to you...