How to import HART DTM file of specific devices into plant explorer/control builder?
I want to integrate E & H make HART enable level transmitter with 800xa system.
While adding the HART devices i am not able to find the required DTM file when i am adding it in control struxture in Plant explorer workplace. I have DTM file of the device. How to import that file?
Answers
It is better to look in ABB Fieldbus library if this instrument is already created.
there is a big library with instruments ready to be implemented in 800xa.
if your instrument is not in the list, you need to send your request to ABB DIC ( device integration center) you need to ask your local support.
there is a big library with instruments ready to be implemented in 800xa.
if your instrument is not in the list, you need to send your request to ABB DIC ( device integration center) you need to ask your local support.
Hi i am not sure whether you have installed the device types corresponding to the devices which you are using. Normally the device types are already available in solutions bank along with the DTM library. You have to install the same through a tool Device library Wizard which comes along with 800xA. For your reference with this mail i have attached the DLW manual. I hope you are in 5.1 systems only. If yes this manual is applicable and you can follow the steps to install the device types. Once after installation the object type structure will contains the instances. Then you can instantiate in Control builder. Hope the answer is useful...
Add new comment