The problem with Input scale from Function Designer
In the Function Designer Ver 5.1 RU1 I have a problem when I want to set up the max scale decimal value (like 6.3 for example). To do it I double click on the CBM_AIS block and in the SignalParameter window (see the attachment SignalParameter.jpg) I change the value Scaling max - 6.3. After this I generate the diagram. In the ControlBuilderM in the properties of this channel I have 6.0 (see the attachment Hardware.jpg). Anybody knows as to solve this problem?
Voted best answer
This is a known issue,
Decimal part of the value for Maximum and
Minimum properties in
CBM_ SignalParameter
aspect is truncated during allocation of signals
to Control Builder M or exporting the aspect
using Import/ Export tool.
The product bulletin is published in Solutionsbank with the PIN:800xAENS-OL-5101-012.You can access this via the link http://search.inside.abb.com/library/Download.aspx?DocumentID=9ARD120523-201&am
p;LanguageCode=en&DocumentPartId=&Action=Launch
To Get rid of this problem update the system to SV 5.1 Rev B. Or contact the local support organization for temporary fix