How to configure in software, AC500 CPU as Modbus RTU Slave?
How to configure in software, AC500 CPU as Modbus RTU Slave?
Any sample code, screen shot or example would be helpful.
thanks in advance...
Voted best answer
Using Control Builder Plus v2.xx
1 You open the interfaces.
2 Rightclick on the Com1 or/and Com2 and add modbus
3 Dobbelt rightclick on the modbus config
4 Under operation mode you choose slave and add a adress.
The baud rate and the rest should match you master.