How to increase Trend Table area for a single trend display?
Hi,
I am trying to increase the width of Trend Table area but i couldn't able to do that.. Kindly help me to increase the trend table area..
Previously, I have no. of traces :1 , now it has been changed to 04. Trace Colors also assigned in Aspect System Structure under trend display. Now if i open the trend from faceplate, it showing one row as trace area. i need to increase the trace area width for four rows. how to increase and where to increase this?
Answers
It would have been nice if you mention your system and version. In 800xA it should be easy, just check witch template you are using, e.g.:
/Erik
Number of rows in trend table is defined in the Trend Template, see 3BSE030322-510D, page 215, figure 183: change Size in the Table section.
However, depending on trend aspect you may or may not succeed by changing the template. E.g. in early 5.1 you could not get inherited trend aspects in a released library to re-read their templates after you have changed them (the "Revert to template" button is greyed out).
I believe something was changed in the most recent revision(s) on 5.1 to correct this.
As I understand your question, as per default you have one "visible" signal (out of four possible). As I understand your question, you want to change the default "visible" signals from one to four, even though only one (out of possible four) signals are used (as per default). To achieve this, first of all you need to determine which Trend Template that is used (Standard Trend Templates are in [Library Structure]Trend Templates). Next, with admin rights, you can change the number of default visible signals from one to four (if the maximum number is four in the template that you are using). Please note that preferable you should create a project specific Trend Template instead of modifying a Standard Template. You can easily create a project specific Trend Template by making a copy of the Standard Trend Template used and thereafter give it a project specific name.
Thereafter you make (whatever changes necessary) to the project specific Trend Template and remember also to refer to the project specific Trend Template from e.g. the Object Type - Trend Display concerned or from the instantiated objects - Trend Display concerned.
I hope the above will help you
BR Carsten
Add new comment