PM864 Losing Memory after power loss
Everytime their is a power drain or power loss to the controller we have to redownload the program to that particular PM864 .. does anyone have any suggestions as to what would cause this? They are operating in redundancy mode (dual) and i have run them each as primary this did not change anything.
Doesnt show battery alarm on PM864 have changed batteries anyway to new ones and also tested, the batteries seem fine.. we have no UPS connected as it is faulty i will be replacing with a temporary one for now but this still does not resolve the memory loss issue.
Voted best answer
Answers
Looks like your internal battery (Built-in battery back-up of memory) needs replacement.
Frequency -Every 2 Years PM8xx Internal Battery (if fitted) Change battery
Internal Battery
The internal battery is mounted inside the PM8xx processor unit (except PM891). Since the battery is not rechargeable, it is important to exchange it on a regular basis (refer to the Maintenance Frequency Schedule for further details)
3BSE036351-510_en_AC_800M_5.1_Controller_Hardware
Section 5 Maintenance -Replacing the BatteryGreetings
I would say that is backup battery case
to be sure check the battery statues led on the front of the controller
if it red you need to replace the battery
or to install external battery module
also you can keep your application using the memory module
Good luck
Since you say you have already changed the internal batteries, then its more likely you have a problem with the battery connections. Try some contact cleaner and make sure everything looks clean. Also, there may be some settings that control how the controller reacts after a crash that could also affect a start after a power upset. Check these using the IPConfig tool.
In any case, as others have already said, the internal batteries are very unreliable ( IMHO they are junk) and an external battery is strongly recommended. Your other alternative is to load the application onto a CF card. This works very well if the plant is commissioned and the application is not being changed very often.
For redundant CPU's compact flash CF solution is not usable - you can't use CF in this case