Universal controller external to internal setpointi
I am using an universal controller to control flow valve, part of the process that i begin with an internal setpoint of 50 then shift to external setpoint of 70 for 1 min then return to 50 internal, but when i return from external to internal the sp remains 70 !
Voted best answer
There is a parameter "Set point tracking" in 3rd Parameter mask of Controller Function Block. Change it on SPI as adjusted. This should solve your problem.
This option exist to avoid Set Point conflicts when changing from external to internal mode.
Source: 3BDD012514R0501_Functions and FBs