Where can I define the size of overlaps and object displays in 800xA?
Voted best answer
There is no seperate size for overlaps and object displays. There is one thing "Size of a display" (be it overlap or object display). You can set the size from graphic editor.
1) Open Editor
2) click on the background
3) In properties window, you have "Height" and "Width".
Answers
Please take into account that you have 2 types of objects:
Graphic Display
Graphic Elements
Grapahic Display have to be defined regarding the window size of your resolution preferably.
Graphic Elements are the graphics you will use to symbolize your objects in a display, like a motor, valve etc.These are added to the graphic display.
Remember Graphic Display have to main ways of working. one is overlap and the other is replace strategy. with overlap the new graphic display covers the previous one, stacking layers of display over your base display. with replace the base display is always replaced by the newer one.
I am also Looking for Aanswer :
What our customer is Looking is when Graphics display is opened as overlap it should come in a small size, corrently it just open in full size, Is it possible to control the size for scree, when it popup ( Rather than manually dragging it to small size )
by admin Rank: 29 on 7/5/2013 1:52:50 AM | Like (0) | Report
Help in closing your question, by voting to a correct answer.
-Admin