800xA Advant Master System Alram
I am facing following alrams on faceplates in Advant 410 Controllers
SCS03(Side A)
West F&G Sys
I/O error and Output error BOTH PINK/RED AND PCrunning green
Similaray following error in message tab
as
Bypass Management Authorisation Key is operated Pos 2
Output Loop error
Do3-ND3
3B26.9
Voted best answer
If you're not able to crack this yourself, you ought to bring this up with your regional ABB Support center who can forward the question to the SafeGuard Support Group in Norway.
Have you checked if any IO-signal is in error state?
Do you get any system messages when connected to the controller(s) with OnLine Builder?
I'm not sure if the Status List option exists/works in SafeGuard, if it does you should be able find the signal(s) in error and start working on them (open circuit, IO board fault, transmitter fault, etc.). There should also be some diagnostics in the System Alarm list for the controller I believe.
Sorry for not being able to come up with anything more concrete.
/Stefan