AC700F - IP Address - Re-program
We have input the incorrect IP address into an AC700F and cannot find a way to re-program it with the 2016 firmware.
Previously on Freelance 2013 we could remove the battery and power and it would usually default back or dial in over the serial port to manually input the address.
Unfortunalty neither of these work anymore. When using Tera Term (or equivilant software) the AC700F communication isn't working, we get a series of characters which mean nothing.
Any help would be appreciated.
Regards,
Jason
Voted best answer
In Freelance 2016 the baudrate was changed to 19200 for the diagnostic port.
Maybe that is the reason.
Answers
Hi Jason,
Incase of connecting via diag port your controller should be in OFF mode(not in run mode). Try putting controller not in run mode and power off and on, keep heating space bar you should get into configuration mode...
Add new comment