Harmony OPC server configuration
Hi!
Is it possible to test OPC server without hardware?
I installed OPC server, created 3 tags using HOPC Offline utility and verify it, there is no error messages. When i starting opc server and try to apply tag configuration, i get this message: "Error : Unable to load configuration due to a name, address or index conflict. Verify the configuration using the Offline utility."
Status of OPC server in online utility is Offline/
State in HOPC tag explorer is failed, and status info is " A fatal error has occurred within the server".
Is the reason of this that i have no connected hardware, or i make some mistakes in configuration?
This is configuration file:
[HARMONY OPC SERVER]
FILE: "C:\temp1.ucf"
INSTANCE,1
ICIDEF,30000,0,50
VERSION,0
VERIFIED,-1
[HARMONY TAGS]
Index,Tag,Type,Loop,Node,Module,Block,PriorityOrWriteHighPriority,EUorCommandWr
iteDisable,PvZero,SpZero,Span,HighAlarm,LowAlarm,DevLimit,StnType,WordSize,NumI
ndexOrScan,QualModeOrTune,AlarmModeOrTuneInhibit,TagDesc
0,new1,ANALOG,1,1,2,500,0,0,0,0,0,0,0,0,0,0,0,0,0,aq
0,new2,ANALOG,1,1,2,501,0,0,0,0,0,0,0,0,0,0,0,0,0,aq1
0,new3,ANALOG,1,1,2,502,0,0,0,0,0,0,0,0,0,0,0,0,0,aq1
Answers
In order to be able to read any HOPC Tag via Client The Harmony OPC Server must be Online so you will need a IET800 or CIU.
It sounds like the Tag Database has a Config issue as well. What HOPC Version are you using ?
Do you have a Valid License ?