Acknowledge in AckState missing, 800xA Advant Master Alarmlist
Hi all,
we have a problem in a new "800xA SV5.1 FP4 for Advant Master" installation.
In the alarmlist for Advant process alarms the acknowledge field in AckState is missing.
It is only a color field.
If I add MB300 system alarms to the same list, the acknowledge for this alarms is available.
In the attached screenshot you can see the problem.
BR, Detlev
Voted best answer
This is typical if an alarm is not regarded as an alarm but only as an event. This depends on the event treatment of the object in the advant database, which points to an event set. Have you properly installed all the EVENT sets in the RTA board?
Add new comment