Advant Controller 450 - Erroneous start-up of redundant CPUs
Problem:Solution
A description of this resolution:
"Advant Controller 450 - Erroneous start-up of redundant CPUs" resolves the following:
A description of this resolution:
- See Solution and Correction
Solution
If one or both CPUs have failed to start-up correctly try manually a warm start or if the memory is corrupt use a cold start.
Correction
The error is corrected in the Advant Controller 450*1.0/5 and in Advant Controller 450*1.1/1 (QC02-BOB21 is revised to *7.0/2).
[ref SR6001 VASMASOITA0120 ]
"Advant Controller 450 - Erroneous start-up of redundant CPUs" resolves the following:
- One or both CPUs might indicate “05” on the CPU display after start-up
The boot block, QC02-BOB21*7.0/0 and *7.0/1, in combination with the mentioned boot proms can cause an erroneous start-up of a redundant pair of CPUs (PM510 or PM510V). One or both CPUs might indicate “05” on the CPU display after start-up. The error can occur at start-up after the command ECONFIG/DICONFIG or after a power failure.
Product concerned
Advant Controller 450 *1.0/x x = (0, 1, 2, 3), 4
Advant Controller 450 *1.1/0
Software concerned
QC02-BOB21*7.0/y y = 0, 1
Hardware concerned
PM510 3BSE000270R0001, PR:K
PM510V08 3BSE008573R0001, PR:A
PM510V16 3BSE008358R0001, PR:A
The above mentioned PM510 and PM510Vxx contain boot proms with the following identification numbers: 4911 014 - RSR, - RSS, - RST and - RSU.
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution:
Add new comment