MasterPiece 200/1 Error in PC element KEYB-N1 (MasterView 100)
Problem:Solution
A description of this resolution:
"MasterPiece 200/1 Error in PC element KEYB-N1 (MasterView 100)" resolves the following:
A description of this resolution:
- Avoid the combination of KEYB-N1 and DSHM 120 strapped to 00.
This error will not be corrected.
[ref FKP1020 VASMASOITA0250 ]
"MasterPiece 200/1 Error in PC element KEYB-N1 (MasterView 100)" resolves the following:
- DSHM 120 strapped to address 00
The PC element KEYB-N1 will not function properly if it has the UNITNO F1 = X00 (X=bus no) and if the keyboard DSHM 120 corresponding to it is strapped to address 00.
Symptom:
If F1=X00 it is not possible to input a value on DSHM 120 that is composed of 2 equal digits in a row e.g. 11 or 88.
PRODUCT CONCERNED
MasterPiece 200/1*3.0/x
SOFTWARE CONCERNED
QMP240 SW*5,0/x
QMP260 SW*5.0/x
QMP280 SW*5.0/x
QAC280 SW*5.1/x
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution:
Add new comment