MasterPiece 200/1 Error in PC elements POS-O and POS-A
Problem:Solution
A description of this resolution:
"MasterPiece 200/1 Error in PC elements POS-O and POS-A" resolves the following:
A description of this resolution:
- See SOLUTION and REVISION
SOLUTION
A. If the board is activated by another PC-element (e.g. POS-A) then it will work properly with POS-O until it is deactivated.
B. With all DSDP 140A in the racks there will be no system messages.
REVISION
The errors will be corrected in the next revision of MasterPiece 200/1*2.0 and in the revision MasterPiece 200/1*2.1/2.
[ref TMP9075 VASMASOITA0314 ]
"MasterPiece 200/1 Error in PC elements POS-O and POS-A" resolves the following:
- MasterPiece 200/1 Error in PC elements POS-O and POS-A
A. PC element POS-O
The element does not activate the board DSDP 140A. This means that the function ON/OFF control can not be used.
B. PC-element POS-A and POS-O
When the command DIBM (DIsable Build Mode) is used the element checks if there is any board at the address given in the element. Normally if the board is missing this will be reported to the operator with a system message.
If the board is missing the existing error will instead cause a serie of system messages. About each second a message will be sent saying "hardware is found" immediately followed by another message saying "hardware is missing". The message stream will cease when the board is placed properly in the rack.
PRODUCTS CONCERNED
MasterPiece 200/1*2.0/11
MasterPiece 200/1*2.1/0
MasterPiece 200/1*2.1/1
SOFTWARE CONCERNED
XMP260 SW*3.0/3
XMP240 SW*4.0/0
XMP260 SW*4.0/0
XMP280 SW*4.0/0
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: