Documentation error - Advant Controller 110*2.0, Errors in RCOM User’s Guide
Problem:Solution
A description of this resolution:
"Documentation error - Advant Controller 110*2.0, Errors in RCOM User’s Guide" resolves the following:
A description of this resolution:
- CORRECTION
Page 3-22
In table 3-6 ’Description of the DB element CI532’ the allowed value ’2-10’ for POSITION is wrong. The correct value for POSITION is 2-20.
Page 3-27
In table 3-8 ’Description of the DB element MVICHAN, communication part’ the recommended value ’96000/bitrate(s)’ for POLLCYCL is wrong. The correct recommended value for POLLCYCL is 96000/SPEED.
The allowed value ’0-255s’ for POLLCYCL is wrong. The correct allowed value for POLLCYCL is 0 - 770s.
Page 3-28
In table 3-9 ’Description of the DB element MVICHAN, parameter part’ some of the specified allowed values are wrong.
The correct allowed value for PARAM1 is 1 - (IL) (instead of 1 - 15).
The correct allowed value for PARAM2 is 0 - (IL) (instead of 10s - 200s).
The correct allowed value for PARAM3 is 0 - (IL) (instead of 1 - 100s).
The correct allowed value for PARAM6 is 0 - (IL) (instead of 0- 100000s).
The correct allowed value for PARAM7 is 0 - (IL) (instead of 1 - 12).
The correct allowed value for PARAM8 is 0 - (IL) (instead of 1 - 100000s).
In table 3-9 ’Description of the DB element MVICHAN, parameter part’ the description of PARAM5 is not complete. The following text must be inserted in row PARAM5 at the end of description for ’Clock setting mode’:
NOTE: For dial-up lines the slave must be dialed-up at least every 4000s to guarantee proper time synchronization.
In table 3-9 ’Description of the DB element MVICHAN, parameter part’ the description of PARAM6 is not complete. The following text must be inserted in row PARAM6 at the end of description for ’Master mode’:
NOTE: Do not use more than 4000s to guarantee proper time synchronization.
Page 3-73
The formula for T poll_cycle must be changed in the following way:
T poll_cycle = N ·
(
1200
S
+ 0,2
)
+ 3
In addition the following text has to be added:
T poll_cycle must not exceed 20s.
Page 3-74
Sentence in section ’Variant 2’:
“The generation of an event can be realized on the master by reading the terminals Q_EMPTY of all EVS elements via a MVB.”
Correction:
“That an event was generated on a slave can be recognized on the master by reading the terminals Q_EMPTY of all EVS elements via a MVB.”
Sentence in section ’Variant 2’:
“It is recommended to specify a cycle time of more than 5 seconds for this MVB because the reading of the Q_EMPTY terminals should brake the event transmission.”
Correction:
“It is recommended to specify a cycle time of more than 5 seconds for this MVB because the reading of the Q_EMPTY terminals should not suppress the event transmission.”
[ref SR6029 VASMASOITA0385 ]
"Documentation error - Advant Controller 110*2.0, Errors in RCOM User’s Guide" resolves the following:
- Documentation error - Advant Controller 110*2.0, Errors in RCOM User’s Guide
MANUALS CONCERNED
RCOM Advant Controller 110 User’s Guide
3BSE 003 181R0001
PAGES CONCERNED
Page 3-22
Page 3-27
Page 3-28
Page 3-73
Page 3-74