Documentation error - Advant Controller 110 PC Elements Reference Manual. Execution times for ADD-MR, OSC-B, PDP, REG and TIMER
Problem:Solution
A description of this resolution:
"Documentation error - Advant Controller 110 PC Elements Reference Manual. Execution times for ADD-MR, OSC-B, PDP, REG and TIMER" resolves the following:
A description of this resolution:
- CORRECTION
on page 12:
ADD-MR the typical execution time is:
(37 + 33xC1 + 44xC2) µs
on page 14:
OSC-B the typical execution time is:
36 µs
PDP the typical execution time is:
406 µs
REG the typical execution time is:
(30 + 7xC2) µs
on page 15:
TIMER the typical execution time is:
(60 + 28xC1) µs
[ref SR7012 VASMASOITA0379 ]
"Documentation error - Advant Controller 110 PC Elements Reference Manual. Execution times for ADD-MR, OSC-B, PDP, REG and TIMER" resolves the following:
- Documentation error - Advant Controller 110 PC Elements Reference Manual. Execution times for ADD-MR, OSC-B, PDP, REG and TIMER
MANUAL CONCERNED
PC Elements Advant Controller 100 Series Reference Manual
3BSE 000 504 R0201
PAGES CONCERNED
The pages: 12,14,15
Corrected PC-elements: ADD-MR, OSC-B, PDP, REG, and TIMER
- Article imported from the previous version of KnowledgeBank