Advant Controller 70 - Some DPS820 Terminals Not Allowed To Be Displayed In Test Table
Problem:Solution
A description of this resolution:
"Advant Controller 70 - Some DPS820 Terminals Not Allowed To Be Displayed In Test Table" resolves the following:
A description of this resolution:
- Do not display for example the DB element DPS820:POSSAMP in the test table.
This restrictions will be added in
Data Base Elements
AdvantĀ® Controller 70
Reference Manual
3BDS100593R101 Rev A
[ref SR1062 VASMASOITA0498 ]
"Advant Controller 70 - Some DPS820 Terminals Not Allowed To Be Displayed In Test Table" resolves the following:
- Advant Controller 70 - Some DPS820 Terminals Not Allowed To Be Displayed In Test Table
Displaying the following DP820 flags in FCB Test Table as DB terminal (e.g. DPS820:SYNCRDY) affects the function of DP820.
POSOF
SYNCRDY
COINC
POSSAMP
SSAMP
The flags are reset when the DB terminal is displayed in FCB Test Table, this is the same behaviour as reading these flags with a PC element.
When displaying POSSAMP and SSAMP the flags are reset, and "disable freeze" is set, i.e. the frozen values at POSMV and SPEEDMV continue counting.
This has the same effect as reading those flags with a PC element.
PRODUCTS CONCERNED
Advant Controller 70*1.2/0
Advant Controller 70*1.2/1
- Article imported from the previous version of KnowledgeBank