Advant Station 100 Series ES / MasterAid 220 - PC element FAULT, FIFO-RW and KEYB-GR, terminal connections
Problem:Solution
A description of this resolution:
"Advant Station 100 Series ES / MasterAid 220 - PC element FAULT, FIFO-RW and KEYB-GR, terminal connections" resolves the following:
A description of this resolution:
- The errors will be corrected in the next main revision of the software. See also Workaround
Workaround
Enter connections numerically instead of symbolic terminal names.
(Showed here with example from FIFO-RW).
1. To avoid problems with source code dumping and loading, use the command SLNUM before the DUPCS command. All PC connections, internal and to database will be numerical.
After DUPCS reset to SLSYM.
When loading with TRPCS no extra measure has to be taken.
2. To use an existing Source Code dump, it is usually faster to edit the source code before loading it rather than correct the errors after loading. The built in editor is adequate if the file size is not very large. Hints: Numeric keypad "-" takes you to all "OR" occurances;
Or press ESC first and then change OR1 to 14, OR2 to 24, OR3 to 34 and so on.
When the occurance is not a FIFO-RW connection press CTRL-S to come to the next occurance of "OR"
[ref SR5030 VASMASOITA0522 ]
"Advant Station 100 Series ES / MasterAid 220 - PC element FAULT, FIFO-RW and KEYB-GR, terminal connections" resolves the following:
- Advant Station 100 Series ES / MasterAid 220 - PC element FAULT, FIFO-RW and KEYB-GR, terminal connections
When using version *1.4/0 and *1.4/1 of Command Oriented Functions in Engineering Station 100 (or MasterAid 220) and corresponding versions of Online builder, to connect
- FAULT terminal INDx, an error occurs and connection takes place to Ix instead.
- FIFO-RW output ORx, an error occurs and connection takes place to Ox output instead (OR1 is usually connected correctly).
- FIFO-RW input IWx, an error occurs and connection takes place to Ix input instead.
- KEYB-GR output ACTCx, an error occurs and connection takes place to output ACTx instead.
The problem does not occur if connection is done numerically, i.e. :24 instead of OR2 in PC element FIFO-RW.
PRODUCTS CONCERNED
Advant Station 100 Series ES
Advant Station 500 Series ES
Advant Station 500 Series OS with Online Builder
MasterAid 220
The PC element FAULT, FIFO-RW and KEYB-GR are found in the following products
- MasterPiece 200/1
- Advant Controller 410
- Advant Controller 450
SOFTWARE CONCERNED
QMA221*1.4/1
Online Builder *1.2/1
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: