AMPL Control Configuration, Control Builder A, Function Chart Builder - Wrong execution when Regional Settings "English US"/Decimal symbol ","/Digit grouping symbol "."
Problem:Solution
A description of this resolution:
"AMPL Control Configuration, Control Builder A, Function Chart Builder - Wrong execution when Regional Settings "English US"/Decimal symbol ","/Digit grouping symbol "."" resolves the following:
A description of this resolution:
- The problem will be fixed in the next release of Control Builder A. See also Workaround
Workaround
Use the default Regional Settings/Regional Options:
Regional Settings (Win NT)/General (Win 2000):
English (United States)
Number(s): Decimal symbol "."
Digit grouping symbol ","
[ref SR1162 VASMASOITA0568 ]
"AMPL Control Configuration, Control Builder A, Function Chart Builder - Wrong execution when Regional Settings "English US"/Decimal symbol ","/Digit grouping symbol "."" resolves the following:
- AMPL Control Configuration, Control Builder A, Function Chart Builder - Wrong execution when Regional Settings "English US"/Decimal symbol ","/Digit grouping symbol "."
If Regional Settings (Win NT)/Regional Options (Win 2000) are set to:
Regional Settings (Win NT)/General (Win 2000):
English (United States)
Number(s): Decimal symbol ","
Digit grouping symbol "."
(Default values are
Number(s): Decimal symbol "."
Digit grouping symbol ",")
then constants entered in exponential notation lose their exponent and the decimal digits.
The application works with wrong constants.
The problem is not visible in offline mode or AMPL Source Code. Wrong values can be seen in online mode when a value containing exponent and/or decimal digits is selected for display.
To correct the problem the default regional settings for English (United States) (see above) have to be set and new target code has to be created and downloaded.
There is no problem when Regional Settings/Regional Options are set to:
Regional Settings (Win NT)/General (Win 2000):
German (Standard)/German (Germany)
Number(s): Decimal symbol ","
Digit grouping symbol "."
These are the default settings.
PRODUCTS CONCERNED
Control Builder A (CBA), version 1.0 and 1.1
AMPL Control Configuration (ACC), version >= 1.7
AMPL Control Configuration Advanced (ACC) 1.7
AC 100 Series Controller e.g. AC 55, AC 70, AC 110, AC 160 all versions.
SOFTWARE CONCERNED
Function Chart Builder, version 4.7, 4.8, 5.0, 6.0 and 6.1.
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution:
Add new comment