MasterPiece 100 - The PC-elements SHIFT and SHIFT-L
Problem:Solution
A description of this resolution:
'MasterPiece 100 - The PC-elements SHIFT and SHIFT-L' resolves the following:
A description of this resolution:
- The error will be corrected in the next MasterPiece 100 revision.
Workaround: To avoid an inverted Boolean input signal use the PC-element INV to invert the signal.
[ref TMP0038 VASMASOITA0658 ]
'MasterPiece 100 - The PC-elements SHIFT and SHIFT-L' resolves the following:
- MasterPiece 100 - The PC-elements SHIFT and SHIFT-L
The PC-element SHIFT doesn’t work if an inverted Boolean signal is connected to one of the inputs IF or IB resp.
The PC-element SHIFT-L doesn’t work if an inverted Boolean signal is connected to some of the inputs I1 to IC2.
In both PC-elements the inverted signal will be considered as one with undefined datatype.
PRODUCTS CONCERNED
All MasterPiece 100 with the PC-elements SHIFT and SHIFT-L up to and including the release MasterPiece 100*2.2/1
SOFTWARE CONCERNED
All software for MasterPiece 100 that includes the PC-elements SHIFT and SHIFT-L up to and including:
ZMP120*2.3/1
ZMP121*2.3/1
ZMP140*2.3/1
ZMP141*2.3/1
ZMP160*2.3/0
ZMP161*2.3/0
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution:
Add new comment