Documentation error, SuperView 100 - MP 200/1 configuration requirements omitted
Problem:Solution
A description of this resolution:
"Documentation error, SuperView 100 - MP 200/1 configuration requirements omitted" resolves the following:
A description of this resolution:
- CORRECTION
* Page 17; under the SuperView 100 configuration requirements, add the following:
NOTE:
In configurations using MP200/1, the MP200/1 must be equipped with option for MV800/1 functionality in the following cases:
· If the MP200/1 is equipped with a GCOM board for connection to SuperView 100
· If other data than DSC and TSC should be collected from the MP200/1
[ref SR2023 VASMASOITA0821 ]
"Documentation error, SuperView 100 - MP 200/1 configuration requirements omitted" resolves the following:
- Documentation error, SuperView 100 - MP 200/1 configuration requirements omitted
MANUAL CONCERNED
ABB SuperView 100 User’s Manual
3BSE000509R0001
PAGES CONCERNED
Page 17
Configuration requirements
- Article imported from the previous version of KnowledgeBank
Answers