SuperView 900 - Lost Subscription signals
Problem:Solution
A description of this resolution:
'SuperView 900 - Lost Subscription signals' resolves the following:
A description of this resolution:
- The error is corrected in version SV *4.1/4
[ref SR4030 VASMASOITA0826 ]
'SuperView 900 - Lost Subscription signals' resolves the following:
- SuperView 900 - Lost Subscription signals
Subscription answer signals from remote nodes are, at high system load, sometimes lost internally in SuperView. The problems appears when the signals arrive in heavy bursts.
If you suspect that this problem might be occurring in your system, please confirm this in the OBJECT CONTROL DISPLAY verifying that the concerned object(s) are not updated with the correct cycletime.
PRODUCT CONCERNED
ABB SuperView 900
SOFTWARE CONCERNED
SV *4.1/1 *4.1/2 *4.1/3
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: