MasterPiece 200/1 - Display exchange time on MasterView 800 will be increased well above 3 seconds
Problem:Solution
A description of this resolution:
"MasterPiece 200/1 - Display exchange time on MasterView 800 will be increased well above 3 seconds" resolves the following:
The underlying cause is:
A description of this resolution:
- The problem will be eliminated in the next revision of MasterPiece 200/1*2.1.
[ref TMP9202 VASMASOITA0318 ]
"MasterPiece 200/1 - Display exchange time on MasterView 800 will be increased well above 3 seconds" resolves the following:
- Display exchange time on MasterView 800 will be increased well above 3 seconds
During the moments, when the updating of TTD logs causes a heavy load in the MasterPiece 200/1, the display exchange time on MasterView 800 will be increased to values well above the typical 3 sec noted in the Product Guide.
PRODUCTS CONCERNED
MasterPiece 200/1*2.1/x x = 0,1,2,3,4,5
SOFTWARE CONCERNED
XMP200 SW*4.0/y y = 0,1,2,3
The underlying cause is:
- Wrong priority of the TTD logging task
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: