Mixing contacts / initiators in the PEB03 and PEB63 modules
Problem:Solution
A description of this resolution:
"Mixing contacts / initiators in the PEB03 and PEB63 modules" resolves the following:
A description of this resolution:
- Install additional resistor at the contact
If, contrary to the recommendations contained in the Operating Manual, the contacts of binary input modules PEB03/63 are fitted in a mixed configuration (mainly initiators), observe the following instructions:
PEB03: Install a 47kOhm resistor in parallel with the contact.
PEB63: Install a 15kOhm resistor in parallel with the contact.
"Mixing contacts / initiators in the PEB03 and PEB63 modules" resolves the following:
- Hardware
Mixing contacts and initiators in the PEB03 and PEB63 modules is not recommended in the Operating Manual.
In Group 1 the PEB63 is mainly fitted with initiators. Only inputs 6 and 7 are fitted with contacts. Group 2 is only fitted with initiators.
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution:
Add new comment