Operating mode changeover in V8.0 non-bumpless
Problem:Solution
A description of this resolution:
"Operating mode changeover in V8.0 non-bumpless" resolves the following:
The underlying cause is:
A description of this resolution:
- Extension of the instruction lists
Instruction lists of program modules concerned will have to be extended in V8.0A to V8.0E if the constraints apply (Click here for example of an Instruction List).
Hereby the command cells for operator commands in the system image (nominal control situation) according to the applicable command situation (actual situation) are updated.
The error is eliminated from software version 8.0F.
"Operating mode changeover in V8.0 non-bumpless" resolves the following:
- CPL
Changing from operating mode Automatic to Automatic-Override possibly is not done bumplessy in V8.0
The command situation is changed over to that operating command which was input at last in operating modes "Manual" or "Automatic-Override". As far as this one is not identical with the last automatic command the command situation will be changed.
All three CPL system image types (IDF, DOS, LOG) are concerned.
The error occurs in V8.0 to V8.0E inclusive and by change over from operating mode "Auto" to mode "Automatic-Override".
The underlying cause is:
- Software error
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: