Coupling in active stations
Problem:Solution
A description of this resolution:
'Coupling in active stations' resolves the following:
The underlying cause is:
A description of this resolution:
- From SW versions 8.0A the system dialog works non-reactively
In the case of SW versions < 8.0A:
Call coupling functions of the station(s) concerned via configuration dialog individually and newly enter coupling channel. After storing the coupling function(s) data transmission will be restored.
'Coupling in active stations' resolves the following:
- Coupling
After changing station data in the system display of a running active station (operator station, coordinator station) and subsequent STORING all running process point transfers of this station will be interrupted in the case of PC and CIS coupling respectively.
The error concerns active stations (OS, CS) with SW version < 8.0A.
The underlying cause is:
- When storing station data channels are killed
Subsequently, data transmission of couplings in which case Contronic P is SLAVE, is not restarted automatically.
With PLC or Protronic couplings respectively Contronic P is MASTER.
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: