Ready-error in RS in monitoring mode
Problem:Solution
A description of this resolution:
'Ready-error in RS in monitoring mode' resolves the following:
The underlying cause is:
A description of this resolution:
- Replace PCZ28
Replace PCZ28 and put new component from Index 10 onward.
Before replacement of the PCZ28: after the ready-error รจ restart RS.
'Ready-error in RS in monitoring mode' resolves the following:
- Hardware
If a redundancy station is in monitoring mode, ready-error may occur sporadically, however, in a very small probability.
Ready-error is reported with following second message:
SYSTEM 1 READY-ERROR 0007 xxxx
The RS will then stop afterwards (in system display: only cycle level 1 is stopped).
The error occurs with PCZ28 Index < 10 and redundancy station is in monitoring mode.
The underlying cause is:
- Addressing error
Addressing error during copying procedure ZSP1 to ZSP2. The addressing procedure RS/ZSP was changed on the PCZ28.
- Article imported from the previous version of KnowledgeBank
Answers
Cause: Article was imported from the previous version of KnowledgeBank Resolution: