Problem:Solution
A description of this resolution:
"TB840 sensitive for disturbance on the opto-line" resolves the following:
A description of this resolution:
- The problem will be corrected in Product Version PR: G
Workaround
To avoid the problem always have PM861 (AC 800M) and TB840 powered before connecting the fiber optic cables.
[ref SR1158 VASMASOITA0027 ]
"TB840 sensitive for disturbance on the opto-line" resolves the following:
- TB840 PR: A, B, B1, C, and D
TB840 is sensitive for disturbance on the in-coming optical-line and can go to hold-up. In redundant configuration of TB840 both modules can go to hold-up because of disturbance on one of the modules. On-line change of PM861 (AC800M) or TB840 can generate disturbance on the optical line.