Problem:Solution
A description of this resolution:
'CI820 upgrading of new firmware' resolves the following:
A description of this resolution:
- See alternatives below
1. The upgrade must be done off-line
2. Make a small change in the configuration and change back again, this can for instance be a parameter change.
[ref SR1108 VASMASOITA0030 ]
'CI820 upgrading of new firmware' resolves the following:
- CI820 SW *2.0/0 to 2.2/3
There are two problems with upgrade firmware on-line
1. Online upgrade of CI820 SW * 2.0 to 2.2/3 does not work, the backup will not start up.
2. Upgrade from other versions than 2.0 can, only on very rare occasions, get problem. The problem is that the backup will not start up after upgrade and it doesn’t help to change the backup to a module with the new firmware.
- Article imported from the previous version of KnowledgeBank