AC 400 Connect 2.1/1 - Wrong network status in Alarm&Event and Status List
Problem:Solution
- The error has been corrected in AC 400 Connect 2.1/2
[ref 3BSE029820D0003 VASMASOITA0737 ]
- AC 400 Connect 2.1/1 - Wrong network status in Alarm&Event and Status List
Node status messages from Transit nodes are not handled correct. The nodes will not be registered to be up. This will be interpreted as there are no more nodes, so the Alarm&Event Server and Status List Server will shut down.
- Article imported from the previous version of KnowledgeBank