S800 I/O - TY801 Shunt Stick
Problem:Solution
A description of this resolution:
'S800 I/O - TY801 Shunt Stick' resolves the following:
A description of this resolution:
- See Actions and Solution
Actions
The stock of shunt sticks (TY801), both at the sub-supplier and our manufacturing unit, has been inspected and the defect units have been corrected by the sub-supplier.
Solution
Proposed solution:
If the male connector at TY801, is not parallel with the circuit board, bend the contact pins until they are parallel with the circuit board and they fit in the TU844 and TU845.
[ref 3BSE033774 VASMASOITA0901 ]
'S800 I/O - TY801 Shunt Stick' resolves the following:
- S800 I/O - TY801 Shunt Stick
Some of the shunt sticks TY801 are difficult to mount in the TU844 and TU845, the maleconnector at TY801 does not fit in the female-connector at TU844 and TU845. The problem occurs when the male-connector at the shunt stick TY801 is not parallel to the circuit board it is attached to.
- Article imported from the previous version of KnowledgeBank
Add new comment